Home  5  Books  5  GBEzine  5  News  5  HelpDesk  5  Register  5  GreenBuilding.co.uk
Not signed in (Sign In)

Categories



Green Building Bible, Fourth Edition
Green Building Bible, fourth edition (both books)
These two books are the perfect starting place to help you get to grips with one of the most vitally important aspects of our society - our homes and living environment.

PLEASE NOTE: A download link for Volume 1 will be sent to you by email and Volume 2 will be sent to you by post as a book.

Buy individually or both books together. Delivery is free!


powered by Surfing Waves




Vanilla 1.0.3 is a product of Lussumo. More Information: Documentation, Community Support.

Welcome to new Forum Visitors
Join the forum now and benefit from discussions with thousands of other green building fans and discounts on Green Building Press publications: Apply now.

The AECB accepts no responsibility or liability for any errors or omissions in the content of this site. Views given in posts are not necessarily the views of the AECB.



    • CommentAuthorbentheball
    • CommentTimeJan 11th 2013
     
    Hi all,
    Looking for some advice/feedback on the following situation.
    I've just air tested a house where we achieved a result of 3.18 @ q50.
    Not bad you might say but the target value was only 6 and the house has NOT been fitted with any mechanical ventilation system. It is fitted with standard trickle vents etc.
    The building code in Scotland basically says that any house that achieves a result of less than 5 @ q50 should be fitted with a mechanical ventilation system or similar.
    I haven't spoken with BC yet but I'm wondering if there is any other guidance out there on air tightness and when additional ventilation is required. The ACH rate @ 50PA is 4.226. Do you think a MV is really required with this result??
    Any pointers would be greatly appreciated.

    Ben
    • CommentAuthortony
    • CommentTimeJan 11th 2013
     
    The house is not too tight.

    If you have fitted trickle vents, fans etc I doubt the BI will put two and two together so you will be alright

    You are likely the only one in this position.
    • CommentAuthorbentheball
    • CommentTimeJan 11th 2013
     
    I spoke with Stroma and they advised that a result of less than 3 requires additional ventilation. The code basically advises that MV is installed where you are designing to achieve a result between 3- 5 (in case you achieve a result less than 3) etc..It would appear air tightness is a pretty hard thing to quantify at the design stage if you are aiming for anything other than very good or very poor. Another thing that may interest a few folk is that this house had no additional vapour barriers installed. The basic constrcution was; concrete floor, 6inch timber frame with 25mm rigid insulation over inside face, plain PB to ceilings and that's it. It was however a very basic single storey box with 4 corners..
    • CommentAuthortony
    • CommentTimeJan 11th 2013
     
    When there is no wind the air leakage of all houses no matter how air tight or how leaky is close to zero.
    • CommentAuthorborpin
    • CommentTimeJan 11th 2013
     
    Ben,

    interested to know if this is a new house or refurbished and what the construction method and or measures taken to get the house airtight.

    I am nearly at the point of getting mine tested as it will be wind and water tight and I want to check it before I start dry lining!
    • CommentAuthorbentheball
    • CommentTimeJan 11th 2013
     
    pretty windy up here 99% of the time so it should be ok!
    • CommentAuthorbentheball
    • CommentTimeJan 11th 2013 edited
     
    I'm on Skye so not quite as far North. Are there any testers up there in Shetland? Give me a shout if not.
    The house was a bog standard Norscot bungalow. 4 corners and an ideal layout for achieving a good result.
    Little effort to make the house air tight as the aim was to achieve a q50 result of around 6.
    The walls are 6inch timber frame with 140mm glass between studs. 25mm rigid insulation over the inside face fixed via 50mm battens into the stud. The walls hadn't been lined yet. The joints in the insulation were NOT taped or sealed and there were no additional vapour barriers used anywhere. Concrete floor. The ceiling looked pretty tight but was not taped and filled and again, no vapour barriers. The windows had been ‘foamed’ into the kit as had most of the ducting inlets.
    From the few houses I have tested my opinion is that a well built timber framed house can easily achieve a q50 result of less than 5 with no additional membranes and/or care and attention to air tightness. If you are going down the route of a super air tight house then you should easily achieve a result of less than 3. Where you don’t make additional provision for ventilation I’d watch out that your house isn’t built too tight.
    •  
      CommentAuthorSteamyTea
    • CommentTimeJan 11th 2013 edited
     
    As you have an airtight house would you not just fit an MVHR unit and get the benefit or warmed clean air?
  1.  
    Posted By: SteamyTeaAs you have an airtight house would you not just fit an MVHR unit and get the benefit or warmed clean air?


    You need less than 3ACH@50Pa before an MHRV shows any benefit. Above that, and you're just adding to the ventilation losses (even with the heat recovery), plus there's the running cost of the fans.

    To know if it's too airtight or not, you need to know that actual air change rate in litres/second and compare that with recommended values based on the occupancy level.

    For example, when I did the analysis for Tony's house using hot2000, this is what it came up with for ventilation requirements:

    F326 VENTILATION REQUIREMENTS

    Kitchen, Living Room, Dining Room 3 rooms @ 5.0 L/s: 15.0 L/s
    Utility Room 1 rooms @ 5.0 L/s: 5.0 L/s
    Bedroom 1 rooms @ 10.0 L/s: 10.0 L/s
    Bedroom 2 rooms @ 5.0 L/s: 10.0 L/s
    Bathroom 2 rooms @ 5.0 L/s: 10.0 L/s
    Other 2 rooms @ 5.0 L/s: 10.0 L/s

    AIR LEAKAGE AND VENTILATION SUMMARY

    F326 Required continous ventilation: 60.000 L/s (0.43 ACH)
    Central Ventilation Supply Rate (): 60.000 L/s (0.43 ACH)
    Total house ventilation is Balanced
    Gross Air Leakage and Ventilation Energy Load: 22733.789 MJ
    Seasonal Heat Recovery Ventilator Efficiency: 81.565 %
    Estimated Ventilation Electrical Load: Heating Hours: 1635.585 MJ
    Estimated Ventilation Electrical Load: Non-Heating Hours: 98.895 MJ
    Net Air Leakage and Ventilation Load: 6191.642 MJ


    See if your airleakage test results give the express it in litres/second, then you'll see if you need an HRV or not (I suspect not)

    Paul in Montreal.
    • CommentAuthorRobinB
    • CommentTimeJan 12th 2013
     
    Sounds like we're saying between 3 and 5 ACH is a nomansland. Too tight to ventilate itself and too high for cost-effective MVHR. Also perhaps a bit late to route MVHR ducting?

    Stroma tested our house too and told me our result was equal to a gap in the building of 1 x 50cm. Those numbers might not be 100% right but my point is they should be able to say "add vents to your building that total an area of Xcm2 and your air tightness will go down to 5." You can then choose the best distribution for the vents to total the required area without testing again, and make sure they're closeable in windy weather.

    By the way is there an open fire or stove (ideally room-sealed) as this would change ventilation requirement.
    • CommentAuthorJonti
    • CommentTimeJan 12th 2013
     
    Posted By: Paul in Montreal you need to know that actual air change rate in litres/second and compare that with recommended values based on the occupancy level.

    Paul in Montreal.


    So how do you calculate it if the level of occupancy changes from two to four or visa versa?

    Jonti
    • CommentAuthorjms452
    • CommentTimeJan 12th 2013
     
    Posted By: Paul in MontrealYou need less than 3ACH@50Pa before an MHRV shows any benefit. Above that, and you're just adding to the ventilation losses (even with the heat recovery), plus there's the running cost of the fans.


    Hi Paul,

    Do you have a reference for the 3ACH figure? I see it quoted a lot but have never seen the original quantitative justification - surely this depends on lots of factors SFP, efficiency etc...
  2.  
    Posted By: jms452Do you have a reference for the 3ACH figure? I see it quoted a lot but have never seen the original quantitative justification - surely this depends on lots of factors SFP, efficiency etc...


    I think it's based on fresh air requirements (like the F326 ones posted above). Of course, it depends on the volume of the building, so maybe it's based on some kind of average. Of course, what's "average" in the UK may be quite different than here in Canada, say.

    Posted By: JontiSo how do you calculate it if the level of occupancy changes from two to four or visa versa?


    The occupancy figures are sort of included in the F326 figures shown above - so much per bedroom etc.

    This document http://archive.nrc-cnrc.gc.ca/obj/irc/doc/ctu-n15_eng.pdf has some more information on F326.

    Paul in Montreal.
    • CommentAuthorbentheball
    • CommentTimeJan 12th 2013
     
    Interesting. It appears ACH is really the figure to use when calculating if additional ventilation is required. This means that you could get a q50 result of less than 3-suggesting you need mroe ventilation, but the ACH rate is greater than 3 suggesting it is not required!
    • CommentAuthorJonti
    • CommentTimeJan 13th 2013
     
    Paul in Montreal,

    I probably didn't explain my thoughts clearly enough. I think it has been said on this thread that number of occupants has to be included in the calculations for the size ventilation. Is the number of occupants really relevant? If so, how does PH allow for the household numbers to change?

    Jonti
    •  
      CommentAuthordjh
    • CommentTimeJan 14th 2013
     
    Posted By: Paul in MontrealYou need less than 3ACH@50Pa before an MHRV shows any benefit.


    Posted By: RobinBSounds like we're saying between 3 and 5 ACH is a nomansland. Too tight to ventilate itself and too high for cost-effective MVHR. Also perhaps a bit late to route MVHR ducting?

    Isn't MEV the recommended solution for these less airtight houses? And possibly 'dynamic insulation'? Or some of the passive ventilation systems.