Home  5  Books  5  GBEzine  5  News  5  HelpDesk  5  Register  5  GreenBuilding.co.uk
Not signed in (Sign In)

Categories



Green Building Bible, Fourth Edition
Green Building Bible, fourth edition (both books)
These two books are the perfect starting place to help you get to grips with one of the most vitally important aspects of our society - our homes and living environment.

PLEASE NOTE: A download link for Volume 1 will be sent to you by email and Volume 2 will be sent to you by post as a book.

Buy individually or both books together. Delivery is free!


powered by Surfing Waves




Vanilla 1.0.3 is a product of Lussumo. More Information: Documentation, Community Support.

Welcome to new Forum Visitors
Join the forum now and benefit from discussions with thousands of other green building fans and discounts on Green Building Press publications: Apply now.

The AECB accepts no responsibility or liability for any errors or omissions in the content of this site. Views given in posts are not necessarily the views of the AECB.



    • CommentAuthorJT101
    • CommentTimeJun 10th 2013 edited
     
    Hi Everyone

    Am installing a solar thermal system, and working on the control side of things.

    All the elements have already been chosen and specified based on solar gains and users needs.

    1500l thermal store with solar coil, boiler coil and HW cylinder built in
    8 panel solar thermal system with controls and drain back tank
    Domestic hot water circuit
    3 Towel rails, across three bathrooms
    Polypipe overlay system with manifold
    Gas system boiler

    But I'm a bit lost with the control side. But basically we want to ensure that the UFH can be turned on at certain times e.g. evenings, and sends a signal to the thermal store to replenish when temp drops. Also a bypass for the pump when it gets up to temperature.

    See attached diagram of what I have so far (if you can't see, here is a larger image: http://www.thebreadcrumbtrail.org/gallery3/index.php/Misc-Travel/Eco-Living/Low-Energy-Buildings_001/Heating-Design-PR)

    I know I'm missing things like expansion vessels, pumps, zone valves, by passes. Just don't know where to put them

    If anyone can help me with this, or refer me to some books/websites on the subject or indeeed some good training courses on system design.

    many thanks
    • CommentAuthorpmusgrove
    • CommentTimeJun 10th 2013
     
    It is possible but takes time working it all out from first principles as there are no websites, books or training courses that I know of that cover this type of system. I wouldn't worry about turning on the UFH at certain times just turn it one when the thermal store has sufficient stored energy that you are now saving for the DHW. I appreciate that your drawing is not to scale but the first thing I would do is drop the UFH flow to mid-tank to ensure that you do not run out of DHW. To get the UFH on when the tank has enough energy you need a thermostat with a 15 - 20 degreee gap between it turning on and off (or off and on). Then link the sensor in the tank to the UFH pump so that it comes on when the temperature of the tank at midpoint is about 50 degrees; the pump can then run on demand from the UFH until the tank falls to 30 degrees at which point the pump is starved of electricity and stops. Works fine for me.
    •  
      CommentAuthorSteamyTea
    • CommentTimeJun 10th 2013
     
    Is it worth separating the heating from the hot water, they serve different functions at different times.
    • CommentAuthorborpin
    • CommentTimeJun 10th 2013
     
    The problem I see is that the solar will have trouble heating the upper part of the tank as you are relying solely on stratification.

    Look at the Akvaterm Solar Plus tanks - http://www.akvaterm.fi/eng/Accumulators/AKVA_SOLAR.41.html I really do think these have the best solution. UFH would normally be taken off the bottom half, but if needed can be topped up off the top. Solar will charge the top when hot enough, else the bottom. Use the boiler to heat the top only (as UFH will take it off there if necessary).

    The only addition is a blending valve to mix the boiler input so it can be set to the ideal temperature for max efficiency.

    You do not say how well insulated/airtigh the property is - ideally the UFH should be run as cool as possible, for as long as possible to keep a steady temperature.

    BTW that is an enormous cylinder. Just got a 750L delivered and wow it seems huge!
    • CommentAuthorGotanewlife
    • CommentTimeJun 11th 2013 edited
     
    Hi JT,

    I have recently done pretty much exactly what you are about to do and on a mostly DIY basis. See attached post. A lot of water has flowed through my system since then and it is too late now (1am) to comment on what I have learned and on your post but I'll get around to it - meanwhile have a look at the diagrams and others comments below.

    http://www.greenbuildingforum.co.uk/forum114/comments.php?DiscussionID=3091&page=1#Item_15

    and more here with a pretty pic:
    http://www.greenbuildingforum.co.uk/forum114/comments.php?DiscussionID=5031&page=1#Item_4


    PS Borpin - you pussy, I had to dig a hole in my floor to fit my 2000 ltr tank in :devil:
    • CommentAuthorpmusgrove
    • CommentTimeJun 11th 2013
     
    Solar heats the top of my Solar Plus tank (750l) just fine. Have 8 sq m of flat thermal solar panels.
    • CommentAuthorandy500
    • CommentTimeJun 11th 2013
     
    If the DPS website is still going they do some good schematics for various systems, you can even spec your own.
    I have a miniscule 300 litre store, with two stats and a relay to control the gas input, top stat set at 40, lower stat at 65 - gas boiler fires when both stats call, and stays on until both are satisfied, hence the relay.
    I'm not an expert, but why so big with the store? If a wood batch boiler was in use then it would make sense to be able to store that much heat between burns, but you only have solar and gas - and outside of the summer solar may struggle with 1500 litres imho.
  1.  
    I'm not a heating system designer but I'm a bit concerned about the horizontal (orange?) connection from the boiler to the heating circuit!

    The role of the system boiler is to put heat into the thermal store either: indirectly via a coil (probably no need for an external expansion tank); or directly where the fluid is shared with the boiler circuit, thermal store and heating circuit with a large external expansion tank required if the thermal store is unvented. I have the latter with an unvented 350l thermal store.

    Domestic hot water is taken from the tank-in-tank and, depending on the temperature of the stored water may need to be blended with cold water to achieve a safe temperature. As this has a large quantity of stored water you will probably need a controller that ensures that this DHW achieves a temperature to control Legionella (my system produces DHW via a heat exchanger which avoids this problem).

    A heating circuit takes heating fluid from one or more levels of the thermal store and blends it to achieve the target temperature. In my case, I use a bivalent (4-port) valve to blend between top; middle and return. A simpler option would be to blend from a single level and return. You might want to use separate heating circuits for UFH and radiators as they typically have different temperature requirements.

    If you want an easy life I would suggest taking a serious look at a Viessmann system boiler with a Vitotrol 200 or 300 series controller. These controllers can be extended to handle two separate heating circuits with mixers and also a solar thermal system. The programming options include support for thermal stores (some boiler controllers don't). For various reasons, I went with a Vitotrol 200A and a Resol solar thermal controller. Getting the two to play nicely together was, to say the least, an interesting exercise!

    However, my system is quite modest with a couple of solar collectors, 350l and nine radiators on one heating circuit.

    The system you outline is of industrial proportions and you definitely don't want to be trying to sort out problems after it is installed! There are lots of things to consider in a complete system such as building regulations; expansion vessels; non-return valves; system cleaners; sensor positions; pipe insulation; smart pumps; thermal breaks and so on. A system of your size might want additional equipment such as low loss headers or other stuff.

    Wish I could recommend a good source of information! In the end, I figured it out myself with the aid of manufacturer's technical documentation, an excellent plumber and a good electrician. I'm happy with the results but wouldn't want to go through that again!
    • CommentAuthorhairydude
    • CommentTimeJun 16th 2013
     
    I'm grappling with a similar issue. Circa 8m2 solar thermal panels, input from 2 wood burners plus electric boiler for emergency back up/holidays in winter ( I should be so lucky). 5 bodies in new, well insulated, airtight house with UFH in a 125mm conc floor slab and MVHR.

    I've been getting conflicting advice on thermal store size - some saying stick around 350l as anything bigger would swamp input from ST whilst others say the bigger the better. Any thoughts? I also have struggled to find definitive advice and even M&E engingineers encountered during day job seem unsure!

    I originally considered a log gasification boiler and this would have made a monster thermal store obvious but I simply don't require that much heat so I'm now thinking a 350l store may be more appropriate? Ive been looking at the thermal store option from McDonald engineers in Glenrothes since it allows me to spend my money in the local economy - anyone have experience of them?

    Apologies if this is a post hijack!
    •  
      CommentAuthorSteamyTea
    • CommentTimeJun 16th 2013 edited
     
    Posted By: hairydudeI've been getting conflicting advice on thermal store size - some saying stick around 350l as anything bigger would swamp input from ST whilst others say the bigger the better
    I think it is asking the wrong question.
    What you need to ask is 'What can I reasonably expect the sun to supply'. You need weather data for that rather than the generic kWh.m^-2.year^-1, that tells you very little except how far north you are.
    I think most people will agree that ST works best when sunny, so how often is it sunny every week? and when it is what is the intensity?
    • CommentAuthorhairydude
    • CommentTimeJun 16th 2013
     
    Thanks ST, seems obvious when you put it like that!

    One of my soon to be neighbours kindly runs a weather station (www.sidlawweather.co.uk) which I see contains info on number of sun hours and solar energy. Our site is a little more elevated and is south facing with no overshadowing

    I guess my next question is what calculation process and / or software should I be plugging this info into to guide the design process. Or alternatively, does anyone know a system designer who I can commission to do this if my brain starts to squeak!

    TIA
    •  
      CommentAuthorSteamyTea
    • CommentTimeJun 16th 2013 edited
     
    Go to this page and start downloading the text files, or ask the neighbour if you can get all his data as a text file:
    http://www.wunderground.com/weatherstation/WXDailyHistory.asp?ID=IANGUSDU2&wuSelect=PWS
    Then you can easily chart each day. Cloud cover is part of a chaotic system, but from the data you can work out the probability of when it will be sunny enough for any given week (very hard to to at the daily level, let the MET office do that for you on the 3 day forecast)
    So if we assume that below 400 W/m^2 there is no useful contribution, then you need to count up the times it is above 400 in the given sampling time period (every 10 minutes or 0.167h).
    Find the average intensity at those times.
    Then multiply the two to get your Wh.
    Yesterday you would have got 2820 Wh or 2.82 kWh.
    There are some big assumptions in there though.
    This one is yesterday up your way
    • CommentAuthorpmusgrove
    • CommentTimeJun 16th 2013
     
    Hairydude; we have 8m2 of flat panels and need the 750l Thermal Store and more on sunny days. The thing is that when the sun is shining it is worth making the ost of it. When it is intermittent you can always top up the top with some electricity. You don't say what you want the heat for; if it is only for DHW then 350l may do but you will need a good dumping mechanism to get rid of the excess heat when the sun is out. if it is also for UFH then 350l is way too small. The best software I have found to work out the heat input required and losses is Passivhaus; if there is anything else that has been verified I would be very interested in using it.
    • CommentAuthorhairydude
    • CommentTimeJun 17th 2013
     
    Thanks guys,

    Interesting, our store will serve both domestic hot water and UFH so the advice I've been given that 350litres would suffice seems to be erroneous or certainly conflicting. Pmusgrove, how is your system working in practice (how often is the electric backup required and is it an immersion or a coil from an electric boiler you use?). I assume you mean the PHPP software when you say passivhaus?
    • CommentAuthorpmusgrove
    • CommentTimeJun 17th 2013
     
    The system is working very well. Electric backup hasn't been used for a couple of months apart from one 2 hour burst when we had 5 overnight visitors and I was fearful of running out of DHW. I have two immersions; one at the top for DHW which I control manually with a boost switch (can set 1 to 4 hours so if I forget to turn it off it isn't too expensive) and a second lower down which runs off an Immersun to take power from the PV when it is available. The software is the PHPP which I have found to be much better than the SBEM or SAP offerings. I believe SBEM especially is costing the nation a great deal as it consistently over estimates the possibility of overheating in commercial and residential buildings and forces designers to use air conditioning plant when it is not required.
  2.  
    The downside of a large store is that you can easily end up with a lot of luke warm water. If your need is mainly for domestic hot water then better to match the store size to your daily DHW requirements.

    There is a fundamental conflict when designing a solar thermal system for both underfloor heating and domestic hot water. For UFH you want to start the circulation pump as soon as the panels are above about 25 degrees C as this is all you need UFH, you will collect a lot more heat on most days & lose less to the environment by re-radiation. For DHW you want to start the circulation pump when the panels are above the temperature in the storage tank. This may take a lot longer to be achieved & on some days may never be achieved.

    You can prioritise DHW by waiting to see if the panel temperature gets up to DHW temperatures. However, this may never be achieved & you could be missing out on the chance to provide UFH.

    You can have multiple solar thermal coils in the thermal store or some kind of stratified loading system, but you still need to decide on the strategy as DHW temperatures will never be achieved if you send the solar thermal flow to the UFH.

    One approach could be to have a summer/winter switch which prioritises DHW in summer & UFH in winter, but I've not seen this implemented on standard solar controllers.

    David
    •  
      CommentAuthorSteamyTea
    • CommentTimeJun 17th 2013
     
    It is that conflict between Heat (energy) and Temperature again.
    I can see the sense in a winter summer priority bias but has anyone set up a solar thermal store for just heating and then used any excess to pre-heat the DHW store. Would that make better use of the solar resource and allow you to have a smaller store. Does mean two cylinders are needed, but the combined physical size may be no more than a 350lt one once plumbed in.
    • CommentAuthorarnyj
    • CommentTimeJun 17th 2013
     
    Hi hairydude my thermal store was from a McDonald engineers in Scotland it was put installed in 2006 when my Solar thermal system was put in afterwards I realised I could have had modifications made to it.
    But by then it was too late and in anycase insulating my house has been a bigger priority, we are a superhome now.

    Arnyj
    • CommentAuthorborpin
    • CommentTimeJun 17th 2013
     
    The was discussed at some length on a thread about low temp UFH. A 350L tank is likely to not be big enough in the summer to take all the heat available. I also wonder if, in a well insulated air tight house, if the 2 log burners will not actually over heat the house.

    Personally I think the key in a well insulated/airtight building is to run UFH at low temp. Install a well stratified tank, and top up the top of the tank as necessary for DHW in the winter. That way you can continue to use cheap 'warm' water in the winter for the UFH. If you heat the whole tank by other means, you can no longer make any use of winter sun.
    • CommentAuthorhairydude
    • CommentTimeJun 19th 2013
     
    I note the thoughts about the woodburners but mrs hairydude insists on the woodburners from a visual / character perspective so that is an argument I wont win. What I need to do is find a woodburner with max output to store as opposed to room.
    The UFH is in the structural slab rather than a screed so will work at lower temps with high thermal mass and in-slab temp sensors. This should fit with borpin's suggestion of a well stratified tank with UFH taken from bottom of tank. I'll discuss with Mcdonald.