Posted By: tonyThis causes a disproportional heat loss through the uninsulated area
Posted By: SteamyTeaIts a weighted average

Posted By: brig001Is it like this?
Assume 100m2 house over two floors, loft area = 50m2 and no other thermal bridges.
Fully insulated loft:
50m2 @ U = 0.19, internal 20, external 0.
Loss = 190W
95% good:
47.5m2 @ U = 0.19, internal 20, external 0.
Loss = 180.5W
5% missing:
2.5m2 @ U = 3.76, internal 20, external 0.
Loss = 188W
Total loss through "dodgy" loft:
368.5W
I think 5% is a bit optimistic - ours had 10m2 missing from a 50m2 loft.
So, we went from:
40m2 with 100mm (badly fitted too!):
Loss = 288W
10m2 with nothing
Loss = 752W
Total loss = 1040W
To:
50m2 with 250mm
Loss = 150W
In short, the uninsulated bit dominates in both these cases
Brian.