Home  5  Books  5  GBEzine  5  News  5  HelpDesk  5  Register  5  GreenBuilding.co.uk
Not signed in (Sign In)

Categories



Green Building Bible, Fourth Edition
Green Building Bible, fourth edition (both books)
These two books are the perfect starting place to help you get to grips with one of the most vitally important aspects of our society - our homes and living environment.

PLEASE NOTE: A download link for Volume 1 will be sent to you by email and Volume 2 will be sent to you by post as a book.

Buy individually or both books together. Delivery is free!


powered by Surfing Waves




Vanilla 1.0.3 is a product of Lussumo. More Information: Documentation, Community Support.

Welcome to new Forum Visitors
Join the forum now and benefit from discussions with thousands of other green building fans and discounts on Green Building Press publications: Apply now.

The AECB accepts no responsibility or liability for any errors or omissions in the content of this site. Views given in posts are not necessarily the views of the AECB.



    • CommentAuthorjules
    • CommentTimeJul 4th 2010
     
    We have a fairly standard solar thermal system commissioned this time last year as part of a building project. The system is evacuated tubes (SSE-facing pitched roof, no shading) feeding to the bottom coil of a 250L HWT, controlled by a Resol Deltasol BS controller. But it doesn't seem to be working as it should, and I am looking for suggestions as to what might be the problem.

    The specific problem is that I don't get water as hot as I think I should. Even in the hot and very sunny weather we've had recently (this is Surrey), the temp of the collector on the roof never exceeded 53C, and the water at the bottom of the HWT was closer to 40C. I have experimented with reducing the circulation flowrate from 6 L/min to 2 L/min, which got us to 55C on the roof, and then I increased the temperature differential at which the pump kicks in to 20C (ie collector 20C hotter than HWT before heat is removed from collector) allowed the collector to 60C today... but the HWT was still close to 40C. All this means that except on the very sunniest of days in midsummer, I have needed to use the boiler to get the HWT up to temperature. That can't be right: my tubes simply don't seem to be collecting enough heat. So does anyone have any suggestions as to what might be the problem?

    [Regarding installation, builder employed installer, we then fell out with builder, as did installer (he didn't get paid). This has consequences for come-back against installer whom I did not contract directly - I have asked them to come and have a look, but am not confident of being able to force them. The main practical consequence of this dispute was that the v long pipe run from tubes on roof to HWT (c15m) apparently wasn't fully insulated (installer stopped work, builder boarded over wall). That obviously doesn't help, but may or may not be relevant to this problem.]

    Thanks in advance for any ideas...
    • CommentAuthorbrig001
    • CommentTimeJul 5th 2010
     
    Hi Jules,
    How big is your collector and what sort is it?
    Are you using the hot water during the day?
    Insulation of the pipes from the collector is very important because of the low powers involved from the collector. How much do you think is missing?
    Brian.
    • CommentAuthorjules
    • CommentTimeJul 5th 2010
     
    Brian
    Collector is 30 tubes, but I don't have any info about it otherwise. We often use virtually no hot water during the day.

    The main thing is that I have absolutely no idea what sort of temps I should be seeing in the collector on a sunny day. If I had been seeing very high temps combined with low temps in the HWT I would immediately have assumed that excessive heat loss in the ong pipe run between the two was to blame, but the collector never gets that hot (except once after a power cut, where with no pump running the temp reached over 130C).
    j
  1.  
    It would be useful to know what diameter the tubes are. Most of the Chinese imported panels seem to be 47mm or 58mm. Assuming the tubes are 47mm the calculation 'tube number x 5 = volume of hot water tank' works well, so 150litres. So it could be the tank is too large causing the low temperatures.

    Hopefully 15mm or preferably 10mm pipe was used, the pipe run length isn't too bad (its about the same here) but it must be well insulated. IIRC you can easily lose 40-50W per m of uninsulated 15mm pipe and the panel is unlikely to have an output over 1.5-2kW.
    • CommentAuthorjules
    • CommentTimeJul 5th 2010
     
    Thanks Megacycles. Will do some measurements tonight, although the pipe between the collector and control unit (which is next to the HWT) is at least 20mm.

    Regarding the tank being too large, I was under the impression that most solar thermal systems produce masses of excess heat in the summer, so that at this time of year it wouldn't be an issue.
    • CommentAuthorevan
    • CommentTimeJul 5th 2010 edited
     
    I use 15 tubes on a 120L tank, i.e about half your system and there has been no shortage of scalding hot water in the last few weeks. It's about a 3m run in insulated 22mm plastic pipe, thermosyphon.

    So I agree you should be getting the tank hot.

    The panel itself can't "not work" so it must be the pipe losses causing the problem I think.
    • CommentAuthorchuckey
    • CommentTimeJul 5th 2010
     
    It looks there are two possible faults, 1, the tubes are not transferring their heat to the water or 2, the water is loosing the heat in the extended pipe run.
    So as for tube faults, is it possible to mount the tubes upside down? or not tighten them properly, as I understand it the heat from an individual tube is conducted via a copper thread into the water filled manifold? Should there be some sort of thermal paste applied to these threads before assembly.
    Loosing the heat fault, this looks more likely. You have some temperature measurements are these built in to your controller or are they what you have measured with your own bit of kit, because if the water is leaving the collector at 55 degs and arriving at the tank at 40 then you truly have some pipe losses. Sounds to me that you should be able to find warm spots on the walls where there should not be any! That long length of insulated piping looks like the problem to me. So you have 15m out and 15m back ! so to my mind you could be loosing 10 deg on the return and 15 degrees on the flow to the tank which, if fixed could give you a nice extra 25 degrees or so.
    This "boarded over" pipework, can you not get to it anywhere? If its run in the cavity of plaster board walls, are they decorated?
    Again thinking out a loud, I wonder if you locate the pipe run with a metal detector/stud locator, you could drill a series of 1/4" holes into the plasterboard cavity and inject expanding foam. Its a very dodgy thing to do as its VERY likely to bulge the plasterboard as it expands. A better way would be to fill the cavity from the top, by drilling a 1" diameter hole into the cavity and filling it with polystyrene beads, but some very long drills will be required to get through the noggins.
    Frank
    • CommentAuthorjules
    • CommentTimeJul 5th 2010
     
    Just to confirm that I have 30 tubes of 58mm diameter and about 2m length. Anyone able to calculate how much heat that should generate on a sunny day in Southern England?

    Thanks for your ideas Chuckey. The HWT temp I'm measuring is the temp of the water in the HWT, not the fluid inside the coil so far as I am aware (the two thermometers, which are part of the kit, are called "collector sensor" and "store sensor"). Therefore if you have say 50-100L of water surrounding the bottom coil in the HWT, you wouldn't expect it to be the same temp as the fluid in the coil (well not initially).

    I am coming to the view that even if there's another fault, I need to insulate the pipe run: it's insulated in the roof, then it's 2.5m down a wall (in a recess), 4m under a bedroom floor, then about 6m along a wall with a false plasterboard wall in front, before the final 2m exposed in the boiler cupboard. I would cut holes in the plasterboard, and then hope to slide the insulating tube along the pipe. It can be done.

    The real question for me is whether the numbers suggest another more fundamental fault with the collector tubes. Despite the problems, the system was tested by the installers when I got them back, but it was more of a pressure test than a temperature test if I recall.
    • CommentAuthorCWatters
    • CommentTimeJul 5th 2010
     
    Power = 4186 * flow * Temperature uplift

    Power is in Watts
    Flow in Liters per second
    Temperature in C

    If the uplift is 20C
    flow rate is 2L/M = 0.033L/S = 0.033Kg/S approx
    then the power collected is

    = 4186 * 0.033 * 20
    = 2.7KW

    But is the flow temperature 60C or is that just the "collector temperature"? Ideally you want some way to measure the actual water flow temperatures rather than pipe or collector temperatures.

    You can also work out how much power is going into the tank the same way, just measure the temperatures at the flow and return near the tank. The difference between what's collected and what's going into the tank should be the loss in the pipe runs.
  2.  
    The 58mm tubes explain the large HW cylinder, you can expect around 50% extra output compared to 47mm, so around 225litres by my calculation - 250litres not too far off then so not a cause of the low water temperature. It sounds similar to a Navitron panel, check their forum - very useful.

    Theres been some debate there for a while regarding panel output, I've seen numbers ranging from 50 to 75W peak per 47mm tube, so a 30 x 58mm panel could give 2.2kW to 3.4kW under optimum conditions. My own rough calculations on my system suggest around 70% efficiency on rare cloudless days (well insulated 30m complete pipe run).

    Heres some rough numbers to consider
    Assuming your 30m pipe run is 15mm uninsulated then you could be loosing 1.5kW (temp differential dependant) so delivery to tank coil could be 0.7-1.9kW. It takes ~12kWh to raise 250litres of water by 40'C, so you may need between 17 and 6 hours of optimal conditions to heat to 60'C
    Using well insulated pipes could reduce the pipework loss to 300W, so heat time reduced to between 6 and 4 hours of optimal conditions, much better!

    Its getting late so you may want to check these numbers over but you can see how important it is to reduce pipe losses on long runs.
    • CommentAuthorjules
    • CommentTimeJul 5th 2010
     
    Thanks Megacycles and everyone else. My pipe run is actually 22mm copper, so presumably heat losses will be greater (curious - how do you calculate?). It sounds more and more as if that lack of insulation is the cause.
    • CommentAuthorbillt
    • CommentTimeJul 6th 2010
     
    An old CH installation book gives pipe heat losses of 47W/M for 15mm pipe and 64W/M for 22mm uninsulated pipe. That's with a temperature difference of 80C, your losses would be a bit less but it's still getting on 1.5kW for 30M of uninsulated pipe.

    Economical have had one of their panels tested and the maximum output for a 30 x 58mm tube panel is just over 1.5kW in full sun with a low cylinder temperature, dropping to about 1.3kW as the water temperature rises. I think those figures are much more realistic than the Navitron guess of up to 3.4kW a panel.
    • CommentAuthorCWatters
    • CommentTimeJul 6th 2010 edited
     
    Not sure if this is an issue but with 2L/min down 15m of 22mm pipe it appears the water takes just over two mins to get from the collector to the water tank.
    • CommentAuthorjules
    • CommentTimeJul 6th 2010
     
    CWatters
    My pump has 3 speeds - 2.5L-min was the lowest, and last night I changed it to the highest, which I'm guessing will be about 8L/min. This discussion has convinced me that collector temp is not important, so prior to insulating the pipe run the only practical thing I can do is to minimise the time taken for the water to make that journey from collector to HWT coil and back.

    Billt, if my panel had a max output of 1.5 kW, and I was losing close to 1.5 kW, then of course I'd be getting no heating at all, which is not the case. So it can't be that bad. Of course heat losses on the return flow must be much lower as the temp difference is much less - say 20C rather than 40C.

    What surprises me in all this is that I had been under the impression that in summer a solar thermal system actually produces loads of surplus heat. According the the figures above - 1.5kW output, 12kWh to raise 250L by 40C, even in a perfectly operating system I'm only just going to have enough heat, and then only on very sunny days. The idea of turning the boiler off for 4 months seems a myth. Is it just because my system is a bit undersized for such a large HWT?
    • CommentAuthorevan
    • CommentTimeJul 6th 2010
     
    I do think you probably have at least 3kW to start with. And losing half of it. If you fix that you'll have a surplus on hot days.
    • CommentAuthorMiked2714
    • CommentTimeJul 6th 2010
     
    Some random thoughts:

    It's probably not the problem, but if possible you might like to check whether the installer used sufficient heat transfer compound on the top of each tube where it sticks in the manifold.

    Also, sadly for you, 22mm pipe is almost certainly overkill, even for a theoretically powerful system like yours. Larger diameter pipes mean more heat loss and more circulating water to heat up every time it switches on.

    Can you use a pipe thermometer to measure the temperature of the circulating water as it goes into the tank coil - this would give you an idea about whether the 15 degree delta T is related to pipe losses or something else.
  3.  
    Hi,

    I’d be concerned about the volume in that pipe. At 15m and 22mm pipe you have just under 6lit in each pipe. When the panel is hotter than the tank and pump comes on a large slug of cooler water (tank to panel leg) is going to go in. This is exacerbated by being cooler than necessary due to lack of insulation. Thus, the panel may not now be sufficiently hotter than the tank and switch the pump off again. Likewise the slug of cooled water in the panel to tank leg will go into the tank coil leaving the hot water from the panel in the leg, where it cools. So forth and so forth.

    It sounds like an complex pipe run so perhaps that’s why it was done on ordinary domestic heating pipe rather than the dedicated (and very expensive) smaller bore and pre-insulated pipe more usually used for panel.

    Don’t forget the coil in the tank would be a 22mm (finned) pipe and could be 15+m in length. Therefore, you have a circuit total of about 18lit.

    Following on from a comment above how long does the pump run each time?

    Cheers
    Mike up North
    • CommentAuthorjules
    • CommentTimeJul 6th 2010
     
    Mike Up N,
    the pump running time depends on the difference between the temp in the collector and that in the bottom of the HWT, and you can adjust what temp difference starts it and what stops it. Installers had set delta T at 6C to start and 4C to stop, but you can increase starting delta T to 20C and have stopping delta T at 5C if you want. Currently I am experimenting with that. Once the pipes are insulated, maybe the answer is fairly rapid cycling, but then that's not necessarily good for the pump.

    You can also adjust the pump speed to alter the time it takes for the water to travel from collector to HWT.

    In other news, I see that Navitron quote 75W/tube as the max output of their 58mm tubes, which would be 2.25kW for 30. And heat loss for uninsulated 22mm copper pipe is 28W/m at deltaT of 22C, and 43W/m at deltaT of 38C. With collector temp below 60C, I reckon my average deltaT over both pipes is about 25-30C, which would give a total loss of around 1kW for 30m.

    I ordered some armaflex pipe insulation at lunchtime. Now I need to make some holes in walls...
  4.  
    Turning the boiler off for 4 months is a myth, you can easily turn if off for 6 months with occasional immersion top-up provided the solar system is installed correctly and the house is well insulated/draught proofed. I'm in Perthshire 200m ASL and a sunny day in February will produce a tank of 50'C hot water although my system is deliberately oversized to cope with the variable conditions here - 60 x 47mm tubes initially heats 180litres and then a 120litre secondary tank.

    It so disappointing to see a professional tradesman make such a fundamental mistake of using 22mm pipework,
    along with dodgy ex DG salesman selling overpriced and overhyped systems, it makes it an uphill struggle convincing the 'man in the street' that this technology really does work when done correctly.

    Thinking positively, the hard work has been done ie the panel and tank are in place, and they are well matched so theres nothing to stop this system working well (you easily have an extra 10-20% insolation). It easy for me to say as I can do the work myself, but if your going through the hassle of exposing the pipework I would remove it and replace with 10mm which is flexible so easy to get round the various corners. I think your always going to see poorer performance because of larger losses and the large system volume, and if you intend to stay in the house the pleasure of a 'solar-bath/shower' in March would soon erode the memories of the hassle. If you can't do the work yourself expose the pipework that needs replacing and get a decent plumber to do the work in December or find a nocturnal one, it shouldn't take more than a day (and send the bill to the installer/builder).
    • CommentAuthorGavin_A
    • CommentTimeJul 6th 2010
     
    Posted By: julesCWatters
    My pump has 3 speeds - 2.5L-min was the lowest, and last night I changed it to the highest, which I'm guessing will be about 8L/min. This discussion has convinced me that collector temp is not important, so prior to insulating the pipe run the only practical thing I can do is to minimise the time taken for the water to make that journey from collector to HWT coil and back.

    Billt, if my panel had a max output of 1.5 kW, and I was losing close to 1.5 kW, then of course I'd be getting no heating at all, which is not the case. So it can't be that bad. Of course heat losses on the return flow must be much lower as the temp difference is much less - say 20C rather than 40C.

    What surprises me in all this is that I had been under the impression that in summer a solar thermal system actually produces loads of surplus heat. According the the figures above - 1.5kW output, 12kWh to raise 250L by 40C, even in a perfectly operating system I'm only just going to have enough heat, and then only on very sunny days. The idea of turning the boiler off for 4 months seems a myth. Is it just because my system is a bit undersized for such a large HWT?

    the heatloss from the pipes is proportional to the temperature of the pipes, so if they aren't insulated properly / at all and it's a long pipe run then it's entirely possible that at lower temperatures the panels will produce enough heat to warm the tank, but as the tank temperature rises, the return temp will also rise and you'll lose more heat on the return (particularly), and the flow (as the flow temp rises) until you basically hit a dynamic equilibrium point where the panel is basically just managing to offset the heatloss in the pipes.


    re the 2nd point... unless you're actually planning to use all 250 litres of hot water every day, you don't need to actually heat the whole lot up each day, just to basically average what you use on average, plus a little bit to offset heat loss from the tank. the extra volume is to store hot water from a sunny day across to a cloudy day, when the hot water from the sunny day will be in a layer of hot water towards the top of the tank, with colder water below it. It's prefectly possible to turn the boiler off for 4 months of the year or more with solar - we're doing 5 people's worth of hot water with the boiler off from mid may to september, other than maybe 2-3 days when there's been no sun for several days in a row.
    • CommentAuthorevan
    • CommentTimeJul 6th 2010
     
    Yes, the uninsulated stuff will limit the peak temperature noticeably.
    I just remembered that I took off a small section of insulation from mine last year to stop it boiling the tank. Like a heat-leak radiator. Still seems to work fine though.