My pump has 3 speeds - 2.5L-min was the lowest, and last night I changed it to the highest, which I'm guessing will be about 8L/min. This discussion has convinced me that collector temp is not important, so prior to insulating the pipe run the only practical thing I can do is to minimise the time taken for the water to make that journey from collector to HWT coil and back.
Billt, if my panel had a max output of 1.5 kW, and I was losing close to 1.5 kW, then of course I'd be getting no heating at all, which is not the case. So it can't be that bad. Of course heat losses on the return flow must be much lower as the temp difference is much less - say 20C rather than 40C.
What surprises me in all this is that I had been under the impression that in summer a solar thermal system actually produces loads of surplus heat. According the the figures above - 1.5kW output, 12kWh to raise 250L by 40C, even in a perfectly operating system I'm only just going to have enough heat, and then only on very sunny days. The idea of turning the boiler off for 4 months seems a myth. Is it just because my system is a bit undersized for such a large HWT?