		<title>Best Spec for EWI retrofit</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=6967&amp;Focus=102261#Comment_102261</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=6967&amp;Focus=102261#Comment_102261</guid>
		<pubDate>Sun, 13 Feb 2011 01:18:05 +0000</pubDate>
		<author>pmagowan</author>
		<description>
			<![CDATA[I now have most of my details worked out and I am now looking at pricing and spec.  I wonder if you guys would put me in the right ball park.<br /><br />Most of my walls are 50cm wide random stone and mortar, the newer parts are 28cm wide block.  I cant get the cost of the different EWI systems online.  I have calculated I will need approx. 1000m2 so it will not be cheap no matter what.  Which system is best and what do they cost for materials? (i know, subjective!).  Which render etc?<br /><br />I think the best system is the continuous insulation and air tight membrane, with cantilevered eaves (see dia).  Do I just mechanically fix the EWI or do I also use adhesive?  Is the final render airtight and can it be joined with the airtight membrane on the roof or is it the adhesive coat between the wall and the EWI that performs this function?<br /><br />Can I use the same insulation board on the roof, above rafters (as in diagram) or is their a different type?  Looking on the web it looks like the whole system is fiddley but not technically difficult.  I was thinking that getting scaffold up and a few handy people you might be able to keep the costs down.  Any one with any experience in this?<br /><br />I have the surveyor coming on wednesday so I would like to be prepared and have an idea on spec.  I estimate my internal area to be about 800m2 so which MVHR and at what cost?  I have really good access to all rooms for ducting so I should thing this would be an easy DIY.  Also I will be doing ground work so underground inlet would be easily installed.<br /><br />I am using a shareware CAD program for the mac to draw up plans and detailing.  If i use local builders then I will need to be very clear on what needs done as I dont think they will be used to this system.<br /><br />Thanks again everyone<br />Paddy]]>
		</description>
	</item>
	<item>
		<title>Best Spec for EWI retrofit</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=6967&amp;Focus=102285#Comment_102285</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=6967&amp;Focus=102285#Comment_102285</guid>
		<pubDate>Sun, 13 Feb 2011 10:57:28 +0000</pubDate>
		<author>jamesingram</author>
		<description>
			<![CDATA[info here.<br /><a href="http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=6910&page=1#Item_17" target="_self" rel="nofollow">http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=6910&page=1#Item_17</a><br /><br />very approx Â£100m2++ for retrofit EWI by supplier/installer ( x1000 wow!)<br /><br />materials for most branded systems approx Â£20-30m2]]>
		</description>
	</item>
	<item>
		<title>Best Spec for EWI retrofit</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=6967&amp;Focus=102293#Comment_102293</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=6967&amp;Focus=102293#Comment_102293</guid>
		<pubDate>Sun, 13 Feb 2011 11:18:52 +0000</pubDate>
		<author>fostertom</author>
		<description>
			<![CDATA[Had v gd pricing from Wetherby, via an experienced contractor. Chris Hirst <a href="http://thinjoint.com/" target="_self" rel="nofollow">http://thinjoint.com/</a> is v helpful as supplier/supervisor (not Wetherby), will travel far from base.<br /><br />Same material can be used for both - but 200-plus thick on masonry walls, only say 100 thick over rafters (or studs) because there it's presumably only topping up between-rafter/stud insulation, preferrably blown-in cellulose fibre (old newspapers) <a href="http://www.excelfibre.com" target="_self" rel="nofollow">http://www.excelfibre.com</a> .<br /><br />Gd idea to OSB over your rafters/studs (can be yr airtight roof membrane) and fix the ERI (external roof insulation) to that nice flat surface. <br /><br />Subject to condensation check, no need for vapour membrane inboard of the insulation, provided you're using low(ish) vapour resistance stuff like EPS (ordinary white EPS (Expanded polystyrene) or grey 'Platinum' EPS - not to be confused with coloured XPS (extruded polystyrene)) or wood fibre <a href="http://www.natural-building.co.uk" target="_self" rel="nofollow">http://www.natural-building.co.uk</a> . Given low(ish) vapour resistances throughout, you can go for a 'breathing' construction in preference to one that has a strong inboard vapour resistance.]]>
		</description>
	</item>
	<item>
		<title>Best Spec for EWI retrofit</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=6967&amp;Focus=102294#Comment_102294</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=6967&amp;Focus=102294#Comment_102294</guid>
		<pubDate>Sun, 13 Feb 2011 11:23:36 +0000</pubDate>
		<author>jamesingram</author>
		<description>
			<![CDATA[Hi , any chance you fancy sharing/whispering wetherbys m2 price supply and fit , for your current project ?<br />I know some retrofit EWI companies looking for Â£150+m2 for just u value up to current regs<br />Cheaper the better i'd say to make EWI really happen big scale.<br />cheers Jim]]>
		</description>
	</item>
	<item>
		<title>Best Spec for EWI retrofit</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=6967&amp;Focus=102298#Comment_102298</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=6967&amp;Focus=102298#Comment_102298</guid>
		<pubDate>Sun, 13 Feb 2011 11:44:03 +0000</pubDate>
		<author>fostertom</author>
		<description>
			<![CDATA[Didn't get it that clear unfortunately, just a big saving kindly offered by the successful contractor, off what I'd spec'd and the best suggested supplier channels that I'd come up with.]]>
		</description>
	</item>
	<item>
		<title>Best Spec for EWI retrofit</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=6967&amp;Focus=102306#Comment_102306</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=6967&amp;Focus=102306#Comment_102306</guid>
		<pubDate>Sun, 13 Feb 2011 12:25:02 +0000</pubDate>
		<author>pmagowan</author>
		<description>
			<![CDATA[Thanks guys.<br />I cant afford Â£100/m2 so going to have to look at DIY/local builders and get materials myself.  Fostertom, I am going for air tightness as well, hopefully to the level where a MVHR unit would be required.  Are you saying that the EWI is essentially airtight?  I currently have sarking board on the old roof and was hoping to only replace what is damaged by leaks etc.  My idea was to put all the insulation on the top just because people on the forum have talked about condensation problems if the airtight membrane is on the cold side of the insulation.  My other thought was that if I get the air tight membrane down quickly then it would provide some protection against a freak shower (I live in N Ireland so these are common).<br /><br />If the EWI is airtight do i just join it to the windows with a bit of tape and plaster over it?<br /><br />My windows are all old sash and very leaky.  My plan had been to DIY fix them structurally but seal them shut.  I have never opened a window in my entire time here!  Then I could put temporary film secondary glazing in until I recover from the EWI cost.<br /><br />How should I conect the hanging eaves to the system? any ideas.  I need to have this all drawn on the CAD and all the detailed parts so that if I use local builders it is simple to understand.<br /><br />Thanks again]]>
		</description>
	</item>
	<item>
		<title>Best Spec for EWI retrofit</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=6967&amp;Focus=102308#Comment_102308</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=6967&amp;Focus=102308#Comment_102308</guid>
		<pubDate>Sun, 13 Feb 2011 12:38:17 +0000</pubDate>
		<author>jamesingram</author>
		<description>
			<![CDATA[re. EWI , check Viking houses detailing for locally available materials and skills as an option<br />also posted eleswhere on forum<br /><a href="http://www.viking-house.ie/timber-frame-warm-stud.html" target="_self" rel="nofollow">http://www.viking-house.ie/timber-frame-warm-stud.html</a><br />some more costing info here<br /><a href="http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=3025&page=2" target="_self" rel="nofollow">http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=3025&page=2</a><br /><a href="http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=3025&page=3" target="_self" rel="nofollow">http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=3025&page=3</a>]]>
		</description>
	</item>
	<item>
		<title>Best Spec for EWI retrofit</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=6967&amp;Focus=102311#Comment_102311</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=6967&amp;Focus=102311#Comment_102311</guid>
		<pubDate>Sun, 13 Feb 2011 13:08:29 +0000</pubDate>
		<author>fostertom</author>
		<description>
			<![CDATA[EWI isn't airtight - I suggested that OSB over rafters could be made airtight. Viking's been mastic sealing them - I favour gapfilling bubble glue-and-screw. So the EWI seal to windows needs to be weathertight but no attempt to make the seal airtight (nor vapourtight).<br /><br /><blockquote ><cite >Posted By: pmagowan</cite>people on the forum have talked about condensation problems if the airtight membrane is on the cold side of the insulation</blockquote>No - important to mentally separate airtight membrane/layer from vapour tight layer/membrane. They may be the same thing but frequently not. Airtight may or may not be vapour tight and vice versa. You've been told to put yr vapour tight membrane (if you have one) inboard of the insulation - but the airtight one can go anywhere in the sandwich.<br /><br />I'm suggesting dispense with the vapourtight membrane, instead go for the alternative 'breathing' construction, in which all elements are of low to low-medium vapour resistivity, but the innermost ones need to have about 5x the resistivity of the outer ones - ideally a gradient of resistivities (note - we're talking resistivities not resistances). In fact I've found in condensation calcs that even that rule can be twisted a bit - as long as the highest (i.e. low-medium) resistivity is placed not further outboard than half way thro the insulation, then it's still OK (but satisfy yourself on this, don't take my word for it). This means that 6 or 9mm OSB3 can be laid over the rafters and approx equal amounts of insulation can be placed both inboard (between rafters) and outboard (over the rafters) of the OSB.<br /><br />Ideally, in fact almost essentially, windows should be placed outboard of extg position (easy if renewing - your problem if not) i.e. mounted cantilever-bracketed outboard within the EWI insulation zone, not touching any of the extg masonry. If left where they are, they'll remain an efficient route for outdoor cold to almost directly contact the extg masonry (which has become part of the indoor environment, inside its 'tea cosy' of EWI/ERI insulation).<br /><br />If planning to extend your eaves, cut off yr extg rafter ends just inboard of the wall EWI, before OSBing over them (incl the cut-off ends). Then lay new extension stub-rafters fixed on top of the OSB (within the ERI zone) cantilevering outward. Lay them out so as to hit-and-miss the extg rafters, but don't rely on the thin OSB to support them - use noggings. This way, the EWI/ERI 'tea cosy' is unbroken, not penetrated by rafter ends. You can hang a heavy cladding e.g. boarding (instead of patent render finish) from those rafter ends.]]>
		</description>
	</item>
	<item>
		<title>Best Spec for EWI retrofit</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=6967&amp;Focus=102312#Comment_102312</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=6967&amp;Focus=102312#Comment_102312</guid>
		<pubDate>Sun, 13 Feb 2011 13:09:36 +0000</pubDate>
		<author>pmagowan</author>
		<description>
			<![CDATA[Thanks James,<br />I dont know how I missed viking houses design in all my searching.  I think it must be because it is timber frame, i just skimmed by.  Do those rafter extensions not produce a thermal bridge or is this negated by the between rafter insulation?  I was looking more at standard batons over the insulation, helping to hold up the eaves which would also be attached to the EWI somehow.  I was still thinking of having all the insulation on top of the rafters.]]>
		</description>
	</item>
	<item>
		<title>Best Spec for EWI retrofit</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=6967&amp;Focus=102314#Comment_102314</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=6967&amp;Focus=102314#Comment_102314</guid>
		<pubDate>Sun, 13 Feb 2011 13:25:45 +0000</pubDate>
		<author>pmagowan</author>
		<description>
			<![CDATA[Thanks Fostertom, just trying to digest what you are saying!  My current roof has tongue and groove pine boards on it.  They are 15mm thick and about 150mm wide.  They seem to produce quite a good smooth surface but I don't think they could be sealed like OSB.  <br /><br />From what you are saying could I put the insulation directly on to them, then put an air tight membrane on top of the insulation.  Would this take away the necessity for two membranes.  My impression is you need a membrane under the slates in order to prevent any leaks from getting in.<br /><br />Your plan with the eaves, is it similar to the Viking house type.  The cantilever rafter stubs cut in to the ERI.<br /><br />I will continue re-reading your post as I need to digest this a bit more!<br /><br />Thanks<br />Paddy]]>
		</description>
	</item>
	<item>
		<title>Best Spec for EWI retrofit</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=6967&amp;Focus=102315#Comment_102315</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=6967&amp;Focus=102315#Comment_102315</guid>
		<pubDate>Sun, 13 Feb 2011 13:30:36 +0000</pubDate>
		<author>tony</author>
		<description>
			<![CDATA[If it were mine I would do 200mm EPX on the walls DIY foam fixed with a high tech paint like render applied over the top on a nylon mesh hopefully all for a fraction of "their" costs]]>
		</description>
	</item>
	<item>
		<title>Best Spec for EWI retrofit</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=6967&amp;Focus=102317#Comment_102317</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=6967&amp;Focus=102317#Comment_102317</guid>
		<pubDate>Sun, 13 Feb 2011 13:35:38 +0000</pubDate>
		<author>pmagowan</author>
		<description>
			<![CDATA[Your windows idea, Fostertom, would be much more effective but I don't think I could do it without costs spiraling.  I have over 20 windows on the ground floor level alone!  I think I have to accept a bit of compromise.  I could chip back the reveals a bit to get more insulation in.]]>
		</description>
	</item>
	<item>
		<title>Best Spec for EWI retrofit</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=6967&amp;Focus=102318#Comment_102318</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=6967&amp;Focus=102318#Comment_102318</guid>
		<pubDate>Sun, 13 Feb 2011 13:38:17 +0000</pubDate>
		<author>pmagowan</author>
		<description>
			<![CDATA[Tony, what would provide the air tightness and what is this high tech render you talk of?  Would it mean I didn't need a plasterer?  I would still have the detailing for around windows etc but I supose you could get them in polystyrene and apply 'render-paint' over them!<br />Thanks]]>
		</description>
	</item>
	<item>
		<title>Best Spec for EWI retrofit</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=6967&amp;Focus=102319#Comment_102319</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=6967&amp;Focus=102319#Comment_102319</guid>
		<pubDate>Sun, 13 Feb 2011 13:39:54 +0000</pubDate>
		<author>fostertom</author>
		<description>
			<![CDATA[<blockquote ><cite >Posted By: pmagowan</cite>I put the insulation directly on to them</blockquote>Sounds good, no need for OSB.<blockquote ><cite >Posted By: pmagowan</cite>then put an air tight membrane on top of the insulation</blockquote>Wherever in the sandwich is best to join up with the wall airtight layer. What are you intending to be yr wall airtight layer?<br /><br />You still need the normal underslating breather 'felt' in addition to all we've been discussing.<br /><br /><blockquote ><cite >Posted By: pmagowan</cite>Your plan with the eaves, is it similar to the Viking house type</blockquote>Yes - but no need for 2 layers of insul over the sarking boards (depends on yr intended thickness) - the cantilevering stub rafters can fill the whole over-sarking insul thickness e.g. 100x50 stubs in 100 EPS. As long as the stubs hit-and-miss the extg rafters, bridging is avoided - but noggings reqd to support the stub rafters at the eave and to prevent uplift of their inboard ends.<br /><br />If extending eaves, how are you going to extend the verges likewise?<br /><br />You don't need all that timber forming a boxed eave (and verge) - your stub rafters can be fully exposed - v attractive - don't even need a downstanding fascia board, instead lay a 75x50 along the top outer ends of the stubs and fix rafter-top galv gutter brackets over it. Nice boarded soffit also laid across the tops of the stubs.<br /><br />Like http://i30.photobucket.com/albums/c301/fostertom/2005-11-10017.jpg]]>
		</description>
	</item>
	<item>
		<title>Best Spec for EWI retrofit</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=6967&amp;Focus=102321#Comment_102321</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=6967&amp;Focus=102321#Comment_102321</guid>
		<pubDate>Sun, 13 Feb 2011 14:02:22 +0000</pubDate>
		<author>pmagowan</author>
		<description>
			<![CDATA[Thanks Fostertom, I am getting a bit closer each time!<br /><br />I don't know about the air-tightness of the walls.  I was hoping I could incorporate it into the EWI somehow.  Do you have ideas?<br /><br />So the airtight membrane could go in pretty much any of the obvious locations and then I also need a breathing membrane under the slates.  Would this need to be held away from everything between batons and counter batons? (too many membranes, my head is fried).<br /><br />I am still getting my head around the hit and miss, idea.  I had thought to directly overlie so that you could screw into the sub rafters giving good support.  The only way you could do this without bridging would be my original idea of the rafter stubs being thin (essentially batons) and overlying the insulation.  Maybe this would not be strong enough!  What holds it up in your example?  Is it the counter batons over the top, as well as attaching to the sarking and with a noggin at the eave?<br /><br />I have not even though about the verges yet!<br /><br />Thanks<br />Paddy<br /><br />PS Thanks for the eaves idea, that has just saved a few quid.]]>
		</description>
	</item>
	<item>
		<title>Best Spec for EWI retrofit</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=6967&amp;Focus=102323#Comment_102323</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=6967&amp;Focus=102323#Comment_102323</guid>
		<pubDate>Sun, 13 Feb 2011 14:13:10 +0000</pubDate>
		<author>fostertom</author>
		<description>
			<![CDATA[Many people use internal wet plaster as the airtight layer on masonry - but a challenge to link that up with roof membrane - and it has to be unbroken across the entire wall surface incl abutting partitions and floor thicknesses and fully accessible so inevitable hairline cracks can be filled as they occur. The latter means you can't rely on external render to do it, if it's hidden under EWI. Don't expect EWI to form airtight layer. It's a problem.<br /><br />Lay breather felt flat over the ERI, lay downslope battens over that (long-screwed thro the ERI) and your slating battens across that. Alternatively, downslope battens first, breather felt draped over that (i.e. sagging between the battens) and your slating battens across that - all normal stuff.<br /><br />Strongly fix noggings between the stub rafters, which will run across and bear on the extg rafters (thro the OSB or in your case T&G sarking boards).]]>
		</description>
	</item>
	<item>
		<title>Best Spec for EWI retrofit</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=6967&amp;Focus=102324#Comment_102324</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=6967&amp;Focus=102324#Comment_102324</guid>
		<pubDate>Sun, 13 Feb 2011 14:16:32 +0000</pubDate>
		<author>pmagowan</author>
		<description>
			<![CDATA[Cool, makes perfect sense now!<br /><br />Do you have anything up your sleeve for the walls and their air tightness?  I was hoping the two could be joined together like the whole house wrapped in cling film and with a big wooly jumper on.<br /><br />Thanks]]>
		</description>
	</item>
	<item>
		<title>Best Spec for EWI retrofit</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=6967&amp;Focus=102325#Comment_102325</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=6967&amp;Focus=102325#Comment_102325</guid>
		<pubDate>Sun, 13 Feb 2011 14:40:19 +0000</pubDate>
		<author>pmagowan</author>
		<description>
			<![CDATA[We are slightly out of sync there, with editing and what-not.<br /><br />I really was hoping that there would be a way to make the EWI system do the air tightness.  I have heard people talk about an initial 'parge' coat of some special stuff but I can't find details.  I cant make the house airtight internally, it would just require too much destruction.  <br /><br />There must be a way.  Externally air tightening a house avoids all the fiddly bits which are bound to fail with time.<br /><br />Thanks]]>
		</description>
	</item>
	<item>
		<title>Best Spec for EWI retrofit</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=6967&amp;Focus=102328#Comment_102328</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=6967&amp;Focus=102328#Comment_102328</guid>
		<pubDate>Sun, 13 Feb 2011 15:50:19 +0000</pubDate>
		<author>jamesingram</author>
		<description>
			<![CDATA[fully coat of EWI adhesive or parge coat externally behind insualtion boards could sort out wall airtightness, differculty is how to transfer this to the roof at wall plate junction . still trying to get my head round this myself.<br />I think by cutting back rafters flush with wall plate as Tom suggested  bringing OSB airtight barrier on top of rafters down to meet external wall behind EWI and seal this join with plate mesh and parge render ?<br /><br />What the cantilever bit re. stub rafters ? got any drawing/pixs]]>
		</description>
	</item>
	<item>
		<title>Best Spec for EWI retrofit</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=6967&amp;Focus=102330#Comment_102330</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=6967&amp;Focus=102330#Comment_102330</guid>
		<pubDate>Sun, 13 Feb 2011 16:17:06 +0000</pubDate>
		<author>MarkBennett</author>
		<description>
			<![CDATA[<blockquote ><cite >Posted By: fostertom</cite>Many people use internal wet plaster as the airtight layer on masonry - but a challenge to link that up with roof membrane - and it has to be unbroken across the entire wall surface incl abutting partitions and floor thicknesses and fully accessible so inevitable hairline cracks can be filled as they occur. The latter means you can't rely on external render to do it, if it's hidden under EWI. Don't expect EWI to form airtight layer. It's a problem.</blockquote><br /><br />Hmm. I am primarily counting on the EWI to form the airtight barrier. I believe that an external basecoat with the insulation boards glued to the basecoat and taped/glued to each other would for a pretty effective airtight layer, even with hairline cracks in the basecoat. using some form of mastic to jon the basecoat to the window/door frames should cover that area.<br /><br />In this scenario, do you really think that hairline cracks in the external render would make much difference?<br /><br />Note I am also planning internal wet plaster, again sealed to all openings as a backup. I wasn't planning to try to seal behind the electrical boxes though.]]>
		</description>
	</item>
	<item>
		<title>Best Spec for EWI retrofit</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=6967&amp;Focus=102331#Comment_102331</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=6967&amp;Focus=102331#Comment_102331</guid>
		<pubDate>Sun, 13 Feb 2011 16:51:28 +0000</pubDate>
		<author>jamesingram</author>
		<description>
			<![CDATA[how about this ?]]>
		</description>
	</item>
	<item>
		<title>Best Spec for EWI retrofit</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=6967&amp;Focus=102332#Comment_102332</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=6967&amp;Focus=102332#Comment_102332</guid>
		<pubDate>Sun, 13 Feb 2011 17:21:17 +0000</pubDate>
		<author>pmagowan</author>
		<description>
			<![CDATA[Some kind of variation on that, yes, James.  The trouble is working out which would be best.  I still think there is a possibility my original idea would work.  200mm of EWI coming up and joining to 200mm of roof insulation.  the air tight membrane could be on the underside of the roof insulation and the 'parge' coat of the EWI.  Then just make up a floating eave attached to a sheet of OSB/ply.  But this up to EWI and attach through the whole system to the OSB/rafter ends under the insulation.  The batons running down the rafters (on top of the insulation) would t hen continue down the rafter stubs and help secure them.<br /><br />I reckon this could be strong enough?]]>
		</description>
	</item>
	<item>
		<title>Best Spec for EWI retrofit</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=6967&amp;Focus=102334#Comment_102334</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=6967&amp;Focus=102334#Comment_102334</guid>
		<pubDate>Sun, 13 Feb 2011 17:31:42 +0000</pubDate>
		<author>fostertom</author>
		<description>
			<![CDATA[<blockquote ><cite >Posted By: pmagowan</cite>make up a floating eave attached to a sheet of OSB/ply.  But this up to EWI</blockquote>Do you mean a sheet of OSB/ply laid flat on top of the ERI? It wd have to be pretty strong - like 25 ply or more - because there's considerable cantilever carrying wind/snow/ladder loads as well as deadweight, and it wd put all that load onto the top outer corner of the EWI/ERI. I think it wd have to be solidly supported at that top EPS corner, or wd crush it in time, leading to eave sag. Still, it's a possible alternative to stub rafters - the downslope battens wd indeed help.<br /><br />Either way, the length running inboard of that point shd be about double the cantilever length - that wd be a large girth of 25 ply! - presumably laid over EPS 25 thinner than the upper roof.]]>
		</description>
	</item>
	<item>
		<title>Best Spec for EWI retrofit</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=6967&amp;Focus=102343#Comment_102343</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=6967&amp;Focus=102343#Comment_102343</guid>
		<pubDate>Sun, 13 Feb 2011 18:49:44 +0000</pubDate>
		<author>pmagowan</author>
		<description>
			<![CDATA[No I mean the OSB attached to the rafter ends where they were cut off at the wall edge.  I would envisage putting similar fixings through as you would need to screw the batons (running with the rafters) through the insulation onto the sarking.  In essence the top part of the EWI would be sandwiched between two pieces of OSB/ply.  I would expect that the way the batons would cantilever the whole unit the forces on the EWI would essentially be compression forces an I would expect it could hold up to this.<br /><br />What do you think?]]>
		</description>
	</item>
	<item>
		<title>Best Spec for EWI retrofit</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=6967&amp;Focus=102346#Comment_102346</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=6967&amp;Focus=102346#Comment_102346</guid>
		<pubDate>Sun, 13 Feb 2011 19:07:10 +0000</pubDate>
		<author>fostertom</author>
		<description>
			<![CDATA[I think I get it - a fascia clamped thro the topmost part of the wall EWI, to the cut-off extg rafter ends - and the downslope battens bridging across? Hm - putting a lot of faith in clamped friction to stop the eave dropping vertically with time. You'd need some kind of cantilever brackets to support it positively. Such things do exist, to carry the weight of heavy EWI claddings, as an alternative to suspending the heavy cladding from the top. Nothing heavier than patent render finish gets supported by the EWI acting in shear.]]>
		</description>
	</item>
	<item>
		<title>Best Spec for EWI retrofit</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=6967&amp;Focus=102364#Comment_102364</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=6967&amp;Focus=102364#Comment_102364</guid>
		<pubDate>Sun, 13 Feb 2011 22:35:56 +0000</pubDate>
		<author>Viking House</author>
		<description>
			<![CDATA[Hi Patrick, Did you considered putting new short rafters on top of the ply?]]>
		</description>
	</item>
	<item>
		<title>Best Spec for EWI retrofit</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=6967&amp;Focus=102366#Comment_102366</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=6967&amp;Focus=102366#Comment_102366</guid>
		<pubDate>Sun, 13 Feb 2011 22:39:44 +0000</pubDate>
		<author>jamesingram</author>
		<description>
			<![CDATA[Is this what you mean pma?<br />how about something like a wall plate strap under or on top of down pitch batton to strengthen ?]]>
		</description>
	</item>
	<item>
		<title>Best Spec for EWI retrofit</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=6967&amp;Focus=102368#Comment_102368</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=6967&amp;Focus=102368#Comment_102368</guid>
		<pubDate>Sun, 13 Feb 2011 22:48:48 +0000</pubDate>
		<author>fostertom</author>
		<description>
			<![CDATA[Still lots of bendy sag potential, looks like 400mm horizontal cantilever, so the EPS will sooner or later end up taking lots of vertical crush, if it doesn't de-bond from the wall face first.]]>
		</description>
	</item>
	<item>
		<title>Best Spec for EWI retrofit</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=6967&amp;Focus=102372#Comment_102372</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=6967&amp;Focus=102372#Comment_102372</guid>
		<pubDate>Sun, 13 Feb 2011 23:39:00 +0000</pubDate>
		<author>pmagowan</author>
		<description>
			<![CDATA[That's pretty much it James.  I have seen your diagram viking and it looks great.  I was trying to avoid cutting in to the insulation with the rafter stubs though. Do you think it is too much weight, fosterom?  Aluminium guttering etc.  You could extend the ply that abuts the EWI to reduce the leverage.  Has got to be good insulation wise.<br />Paddy]]>
		</description>
	</item>
	<item>
		<title>Best Spec for EWI retrofit</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=6967&amp;Focus=102374#Comment_102374</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=6967&amp;Focus=102374#Comment_102374</guid>
		<pubDate>Mon, 14 Feb 2011 00:11:33 +0000</pubDate>
		<author>fostertom</author>
		<description>
			<![CDATA[Not so much the deadweight - that's trivial beside the snow load, ladder load, wind load/buffeting that shouldn't be underestimated during a long life! I'd really beef it up, make everything solidly supported rather than relying on squishy materials longterm.]]>
		</description>
	</item>
	