Home  5  Books  5  GBEzine  5  News  5  HelpDesk  5  Register  5  GreenBuilding.co.uk
Not signed in (Sign In)

Categories



Green Building Bible, Fourth Edition
Green Building Bible, fourth edition (both books)
These two books are the perfect starting place to help you get to grips with one of the most vitally important aspects of our society - our homes and living environment.

PLEASE NOTE: A download link for Volume 1 will be sent to you by email and Volume 2 will be sent to you by post as a book.

Buy individually or both books together. Delivery is free!


powered by Surfing Waves




Vanilla 1.0.3 is a product of Lussumo. More Information: Documentation, Community Support.

Welcome to new Forum Visitors
Join the forum now and benefit from discussions with thousands of other green building fans and discounts on Green Building Press publications: Apply now.

The AECB accepts no responsibility or liability for any errors or omissions in the content of this site. Views given in posts are not necessarily the views of the AECB.



    • CommentAuthorwookey
    • CommentTimeMar 17th 2011 edited
     
    Just came across this doc, suggesting that whilst XPS short-term water absorption is very good, in the long term it aborbs a lot more than EPS (18% after 15 years, reducing thermal resistance to 50% of when new):
    http://www.buildblock.com/pdfFiles/Foam-Control%20EPS-Water%20Absorption%20Facts.pdf

    Do we believe this? Having just filled my foundation with XPS (sirap Gematherm: http://www.sirapgroup.com/insulation/page/download/129 ) I'd like to think that it was rather better than this. That doc specifies 3% absorption (to EN12088, which tests over 28 days).
    • CommentAuthorSaint
    • CommentTimeMar 18th 2011 edited
     
    Absolute garbage. Who is the third party accredited testing authority?
    The only way that XPS can be forced to take in even moderate amounts of moisture is through an extreme vapour diffusion system that is difficult to set up even in a lab.
    I've seen XPS removed after 20 years sub slab high load where the lambda was unchanged but surprisingly the compressive strength had increased
    •  
      CommentAuthorfostertom
    • CommentTimeMar 18th 2011
     
    If garbage, does this mean you can tell any lie and get away with it in US - no ASA? It does sound credible to me.
    • CommentAuthorCWatters
    • CommentTimeMar 18th 2011
     
    Seems to be based on samples from one site..

    http://geosyntheticsmagazine.com/articles/0209_pan5_test.html

    Samples of EPS and XPS were excavated from the exterior foundation of a building in St. Paul, Minn. The insulation was placed into service in 1993 and had 15 years of use as vertical wall insulation separating the heated building foundation from soil.

    “The results of the independent testing are dramatic,” said Todd Bergstrom, VP of Technology for AFM Corp. “The EPS insulation maintained 94% of its stated R-value of 3.6 after the 15-year time period and had a moisture content of only 4.8%.

    “However, the XPS retained only 52% of its stated R-value of 5.0. The loss in R-value for the XPS is quite dramatic and can be explained very simply by the 18.9% of moisture absorption during the 15 years of use. These results suggest very clearly that short-term laboratory tests of water absorption for XPS do not necessarily reflect the long-term, below-grade performance of these materials.”
    •  
      CommentAuthorSteamyTea
    • CommentTimeMar 18th 2011 edited
     
    Seems to be more about the cell structure rather than the material itself. This in turn will make it more or less affected by the environment it is in. So if a less than ideal EPS was used in a wet location then it is possible that water will migrate into the foam structure. This does not mean that every installation will have this problem every time, just that what was checked did. This makes it very hard to compare like for like. But if you take ABS (a type of 'solid' styrene monomer) the 24h absorption is 0.3% and the saturation figure is 0.7%, or 2 1/3rd times. Density of ABS is 1024 kg/m^3, water is 1000 kg/m^3 and air is 1.2 kg/m^3.
    So the solid material can absorb another 72kg/m^3 of water (1096 kg/m^3).
    Some more water will be trapped in the voids between the cells by capillary action/pressure difference, this will be dependant on the overall density of the EPS, but I would guess that it would be at least another 100kg/m^3 (but just guessing there). This would displace air that has a thermal conductivity of 0.025 W/mK with water at 0.6 W/mK or 24 times worse. ABS is 0.17W/mK or 3.5 times better than water.

    So I can easily see that it is possible that what may seem like a small moisture problem can greatly affect the overall performance of the EPS.

    Wookey, what measures have you taken to stop water ingress into the EPS?

    Edit, EPS should read XPS
    Whoops, well spotted Tom, I did, thanks
    •  
      CommentAuthorfostertom
    • CommentTimeMar 18th 2011
     
    ST have you put EPS when you mean XPS? Otherwise, confusing!
    • CommentAuthorwookey
    • CommentTimeMar 18th 2011
     
    One wonders if there are significant differences between different XPS vintages/manufacturers? It's hard to know how representative the stuff put in this building in 1993 is of typical product today. Clearly they (ACH foam tech) are selling their particular brand of EPS, but I find it hard to believe that the report is simply lies. The question really is is there some kind of problem with their testing, and/or how common/current is this issue of slow long-term absorption? If the process is very slow then clearly the ISO/EC/BS 28-day test is not really representative.

    http://www.exiba.org/Properties_of_XPS.asp#Water gives details of the ISO/EC/BS 28-day tests and also says that we know from 20-30 yrs experience that these tests _do_ represent a realistic upper limit.

    So who's right? The most logical explanation of all this is that the stuff from Minnesota in the ACH foam tech report was not as absorption-proof as normal, but this testing probably isn't done very often, so this situation may be more common than we realise, or it may be a complete anomaly.

    Saint, you say you've seen XPS fished out after 20 yrs and the lamda was unchanged. Did someone actually test it? Can you point to any docs on the subject?

    ST - The XPS (not EPS!) in my cavity below DPC has no specific waterproofing features. I am relying on its advertised low water absorption. The XPS below the floor will be above the DPC so that will be protected from moisture in the ground below.
    • CommentAuthorSaint
    • CommentTimeMar 18th 2011
     
    Wookey, testing was done by Frigoscandia on one of their own coldstores. Thermal efficiency, moisture resistance,the vapour resistance and compressive strength of the insulation are major concerns and they used to monitor them closely. XPS supplanted cork as the standard insulation for coldstore floors and retains that position today for those very reasons. Remember also that XPS was originally developed as a buoyancy aid for the US Navy so again resistance to moisture pickup would have been a critical design parameter
  1.  
    Guys,

    Not wanting to hijack the thread but does anyone have any info on how XPS copes with UV exposure. Due to financial constraints our ICF build is running pretty slow and I can see its going to be summer of 2012 before we can render the outside which means the outside insulation would have been exposed to sunlight for over 2 years! Do you think this is a problem, could its thermal properties be effected? It's nearly water tight, tiling roof now but our main problem is getting the windows, hence ideally we wouldn't render until they are in?
  2.  
    Guys,

    Not wanting to hijack the thread but does anyone have any info on how XPS copes with UV exposure. Due to financial constraints our ICF build is running pretty slow and I can see its going to be summer of 2012 before we can render the outside which means the outside insulation would have been exposed to sunlight for over 2 years! Do you think this is a problem, could its thermal properties be effected? It's nearly water tight, tiling roof now but our main problem is getting the windows, hence ideally we wouldn't render until they are in?
    • CommentAuthorSaint
    • CommentTimeMar 19th 2011 edited
     
    Phil, the UV will break down the top layer or couple of layers of cells, maybe <1mm thickness or so. The damaged cells remain as a fairly tightly bound dust on the surface of the boards. This dust then serves to protect the XPS board underneath from further UV damage. Normal recommendations would be to remove dust with stiff brush once you're ready to proceeed with the job and carry on as normal. Little or no effect on the thermal properties other than typical ageing and 1mm less insulation (!). Personally though as its a reasonably long period of time I'd try and drape something over the boards if possible or simply paint with a thin coat of light coloured water based paint (no solvents!!!)